They certainly do exist. Over almost 50 years, our control transformers were almost all 400V in, 110V out.#
Yes, I should have thought about CPTs. Very common application.

They certainly do exist. Over almost 50 years, our control transformers were almost all 400V in, 110V out.#
They certainly do exist. Over almost 50 years, our control transformers were almost all 400V in, 110V out.
retirede /Besoeker3 ,
Thanks for the replies.
I just realized my mistake in interpreting the table. In fact, pretty much all of the equipment in the new factory uses 400VAC to 110 AC stepdown transformers to supply single phase 110 VAC for their control hardware that is both 50 & 60Hz compatible.
Going back to the motor in question;
230/400V Delta/Wye at 50Hz. (3-Phase Motor)
And looking at the table below;
View attachment 22223
If my Supply voltage (Grid Voltage based on the highest voltage listed on column 1) is;
200VAC or 220VAC 3-Phase 4-wire grounded Wye,
OR;
220VAC 3 Phase 3-Wire Delta Connected;I can connect the above motor in DELTA configuration (per 230/400VAC motor spec)
If my Supply voltage is;380VAC or 400VAC, or 415AC or 440VAC 3-Phase 4-wire grounded Wye,
OR;
440VAC 3 Phase 3-Wire Delta Connected;
I can connect the above motor in WYE configuration (per 230/400VAC motor specification)
Or am I still way off?
...
Going back to the motor in question;
230/400V Delta/Wye at 50Hz. (3-Phase Motor)
And looking at the table below;
View attachment 22223
If my Supply voltage (Grid Voltage based on the highest voltage listed on column 1) is;
200VAC or 220VAC 3-Phase 4-wire grounded Wye,
OR;
220VAC 3 Phase 3-Wire Delta Connected;I can connect the above motor in DELTA configuration (per 230/400VAC motor spec)
If my Supply voltage is;380VAC or 400VAC, or 415AC or 440VAC 3-Phase 4-wire grounded Wye,
OR;
440VAC 3 Phase 3-Wire Delta Connected;
I can connect the above motor in WYE configuration (per 230/400VAC motor specification)
Or am I still way off?
He is mixing up supply issues with motor connection issues. A MOTOR certainly does care whether it is CONNECTED internally as Wye or Delta, because (in IEC motors) that is how the motor voltage is determined.A motor won’t care if the supply is wye or delta as long as the voltages match.