steelersman
- Lake Ridge, VA
what is a low point drain?Yep, that's why we always install low-point drains in our conduit systems.![]()
One important point is that you have not said where the VFDs are going to be located; at the line source or near the pumps. In other words, is the 50' before or after the VFDs? If it is after, and the VFD output wires are in the same conduit, you are asking for trouble if they are not properly shielded; the VFD outputs will induce on each other and cause you no end of headaches, likely ending in frying the transistors one one or both drives.
The motors are in a Class I, Division 1 location? They should NOT be driven by an ASD unless the motors are rated for it AND will be operated within the parameters speified.
Otherwise look in the drive specifications for wiring restriction. THHN in conduit should be OK.
The point about checking whether that grinder pump can be run from a VFD is a very good one. Grinder pumps are often expected to provide high starting torque, just in case they have to "munch" something, shall we say, inappropriate(?), on start up. Without over sizing, non-vector VFDs (and even many cheap-o vector versions) will effectively limit starting torque.
Two sets of unshielded VFD output conductors in a common PVC conduit will probably create problems.The VFD?s will be 50? before the pumps, and the existing pump circuits share a 1 ?? PVC that includes EGC from source to destination.
Isn't the EGC good enough to drain any stray voltages or currents?Two sets of unshielded VFD output conductors in a common PVC conduit will probably create problems.
interesting. So basically you need to keep each set of wires in it's own conduit. But what about shielding it?I'ts not a matter of stray voltages or currents, but the high-frequency, chopped wave RF field created in the wiring by a VFD. And having the fields of two drives side by each will affect both drives and motors, with possible release of smoke from motors and drives.
Need proof of the RF a VFD generates? Try to operate a portable radio close to one or it's motor, doesn't matter if it's AM or FM, you'll only get a lot of static.![]()
You can get highly shielded (for lack of a better term) VFD cables from people like Belden and Lapp. They have the 3 conductors triplexed and then covered with an overall shield, protected by a jacket...
aha. I guess I was duped by weressl. And here I thought it had something to do with a drain wire that is usually found inside sheilded cable.It could be a lot of things, for me it is often a small hole drilled in the low point of a raceway, a small cut in the bottom side of a gasket etc.
Check out 225.22
Looks like a Beldon 29501, & cut sheet for 29501, can be used. It?s only #14 but seems to be rated and sized as per NEC.
It?s also only .6 diameter so wire fill won?t be a problem, I?m probably going to suggest this cable.
What's an ASD?
You can have an ASD on a DC system, but a VFD only works on AC.ASD = Adjustable Speed Drive
VFD = Variable Frequency Drive
Same thing. Speed is varied by adjusting frequency.
ASD is the generic term. An ASD could be nothing more than pulleys and belts, although it general means something more complicated like an eddy-current contoller or a variable frequency drive.
Good point. I've only messed with AC systems so I wasn't thinking it through all the way. I've always used the two interchangably. I'll have to be more careful with that in the future.