hhsting
- Glen bunie, md, us
- Junior plan reviewer
I have vfd that has bypass. The vfd manufacturer says input breaker size is 15A and motor full load amps is 11A.
I am not sure how to size breaker since this has bypass. If i consider bypass then i take 11x2.50 has inverse time breaker which come out to 27.5A so next size would be 30A breaker.
Based on NEC 2017 Article 430.130(A)(B) Should their be 30A breaker or 15A breaker feeding the vfd with bypass?