vfd's indide air handler

Status
Not open for further replies.

justinaway1

Member
Location
West Coast
We had to replace motor and upgraded controller to vfd's. The contractor installed vfd's inside air handler. Is this exempt from NEC? I am concerned cuz feeder conductors and control wires are bundled together and they clamped down directly on conductors with supplied 2 screw connector! I'm thinking a violation of 430.73, but was told it must have passed inspection.
 

Mike01

Senior Member
Location
MidWest
Location

Location

Is it a "Packaged Roof-Top"? On another thought remember that VFD's contain electronics that can be temperature seneseative sometimes within rooftops are not the best locations depending on the local that they are installed.
 

justinaway1

Member
Location
West Coast
Yes its a package unit and the vfd's are inside. I dont like the location but apparently the correct rated enclosure was "too expensive" so putting them inside avoided this additional cost.
 