Many thanks to everyone for sharing their knowledge! Gives me quite a few things to try out. I'll try and provide a little more info on what I've tried and what our setup is.
The OP never mentioned that the drives are actually trying to restart. The OP simply said that after a power system 'blip' the drives trip on DC bus overvoltage.
Everything since then has been a guess at what items could cause this type of overvoltage, without ranking them based on probability.
Nailed it.
We have a 4160MCC that supplies power to our 4 main drive motors, as well as 2x 4160 - 480v transformers that feed 2x 480v MCC's.
These drives seem to be the most sensitive equipment we have as far as tripping. There are a few things that cause them to trip, but for the most part its shoddy power coming from the utility that causes it.
-Anytime we are starting any of our main drives (4160V compressor motors: 2x 1750HP and 2x 4157HP) we utilize softstarts on all, and a 6410KVAR capacitor bank for the 4157HP motors. Not as big a deal, although I imagine its not too good for the VFD's.
-If there is ANY slight blip in power. Usually occurs when its windy, these VFD's are the first to trip but everything else stays running.
We had installed a power quality analyzer to see what was going on with our 480v BUS during a start of our 4160 motors.
I recorded the highest and lowest values in the trend:
Spike peak: 517v
Spike dip: 407v
The manufacturer provided a little bit of help, and we tried playing with the flying start settings.
As its setup now, the drive will still trip on DCBUS overvoltage (this is the main issue), and then attempts to restart with the flying start settings tweeked (it restarts without issue). My concern is the drive is tripping for a reason, and to continually trip and program it to auto-reset doesnt seem like the proper way to handle it. I am thinking the best way to address the problem is figure out whats causing the trip (as the trip is implemented to protect the drive) and find a remedy to reduce its reoccurance.
I think the bottom line is our utility feed isnt the greatest and this is whats likely causing our issues. Due to the fact its usually quite windy when we have power blips, you guys have got me wondering if it might also mess with the inertia of the fans and the VFDs ability to control them. There are so many settings and menus on the drive, its hard to tell where I need to start looking!
Edit:
Scratch that. There are a total of 6 VFD's, 3 are fed from one of the two 480 MCC's respectively. For all 6 of them to trip simultaniously, I am now thinking it must most defintely be an issue with the power supplying them that is causing the DCBUS overvoltage.