A few reasons:wasasparky said:...why not?
- 360? is a complete circle....you go past that a bit and you get a knot ~ no wire pull [I know...we can pull through 5 90?...]
- sidewall pressure on the insulation ...you can rupture it with excess pressure
- damage to the conductors themselves...a la...the "wire stretcher" ...although the conductors will probably snap or at the least, you'll lose the nose in the conduit.
Recently I've been involved with some pulls that required both pull calculations as well as a "tensionometer".