Violation?

Status
Not open for further replies.

nickelec

Senior Member
Location
US
Inspector says I'm violating 240.21 secondary tap but won't be more specific. This is currently the set up I have I'm arguing 230.90 A exception 3
Says I can do this
b8810f78d07dddb0ee792d1b3c1fe911.jpg


Sent from my SM-G965U using Tapatalk
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Need a lot more detail to say there is no violation what so ever but I can't see a 240.21 violation.
 

nickelec

Senior Member
Location
US
Thats my point, you could picture the install. SEC come off the meter to feed a bus bar in a double breaker enclosure

Sent from my SM-G965U using Tapatalk
 

suemarkp

Senior Member
Location
Kent, WA
Occupation
Retired Engineer
How can anyone answer the question when wire sizes are not specified since the issue is taps? What is "EB"? Do you have a load calc? Are you under 2020 code or an older one (would be a different issue, not the tap issue)?
 

nickelec

Senior Member
Location
US
2008 code #2 feeding the meter and each enclosure eb stands for end box

Sent from my SM-G965U using Tapatalk
 

suemarkp

Senior Member
Location
Kent, WA
Occupation
Retired Engineer
#2 seems fine if copper. Maybe not if aluminum. Does the load for the full service (the areas covered by all 3 panels) calculate to under 115A (or 90A if aluminum)?
 

nickelec

Senior Member
Location
US
It is copper and yes definitely under 90a all the appliances and heating are gas

Sent from my SM-G965U using Tapatalk
 