Inspector says I'm violating 240.21 secondary tap but won't be more specific. This is currently the set up I have I'm arguing 230.90 A exception 3
Says I can do this
How can anyone answer the question when wire sizes are not specified since the issue is taps? What is "EB"? Do you have a load calc? Are you under 2020 code or an older one (would be a different issue, not the tap issue)?
#2 seems fine if copper. Maybe not if aluminum. Does the load for the full service (the areas covered by all 3 panels) calculate to under 115A (or 90A if aluminum)?