Violation?

Status
Not open for further replies.

nickelec

Senior Member
Location
US
Inspector says I'm violating 240.21 secondary tap but won't be more specific. This is currently the set up I have I'm arguing 230.90 A exception 3
Says I can do this
b8810f78d07dddb0ee792d1b3c1fe911.jpg


Sent from my SM-G965U using Tapatalk
 
Need a lot more detail to say there is no violation what so ever but I can't see a 240.21 violation.
 
Thats my point, you could picture the install. SEC come off the meter to feed a bus bar in a double breaker enclosure

Sent from my SM-G965U using Tapatalk
 
How can anyone answer the question when wire sizes are not specified since the issue is taps? What is "EB"? Do you have a load calc? Are you under 2020 code or an older one (would be a different issue, not the tap issue)?
 
2008 code #2 feeding the meter and each enclosure eb stands for end box

Sent from my SM-G965U using Tapatalk
 
#2 seems fine if copper. Maybe not if aluminum. Does the load for the full service (the areas covered by all 3 panels) calculate to under 115A (or 90A if aluminum)?
 
It is copper and yes definitely under 90a all the appliances and heating are gas

Sent from my SM-G965U using Tapatalk
 