I was running a switchleg for an exhaust fan in a house the other day and came across a receptacle in the kitchen cabinet for the microwave. GC stuck his head up and says, "Everything okay with that?" Didn't think to take a picture, but, here's what I observed:

The receptacle had no faceplate. Article 404.9.A

It was wired with #14 off a 20 amp SABC. Articles 210.19.A.1, 210.19.A.3, 210.23.A.2, 240.4.D.3

Small 3/8" or 1/2" hole drilled into top of plastic box where power was taken. (Didn't go through the factory clamp.) Article 110.3.B

Hole in cabinet through wood and sheetrock into KO in box, no bushing or clamp. Article 317

Ground in "supply" box was was just lightly hooked around the grounds that were there. Can't think of which article applies here.

Did I miss anything? Do you agree/disagree?
 

mcclary's electrical

Senior Member
Location
VA
I was running a switchleg for an exhaust fan in a house the other day and came across a receptacle in the kitchen cabinet for the microwave. GC stuck his head up and says, "Everything okay with that?" Didn't think to take a picture, but, here's what I observed:

The receptacle had no faceplate. Article 404.9.A

It was wired with #14 off a 20 amp SABC. Articles 210.19.A.1, 210.19.A.3, 210.23.A.2, 240.4.D.3

Small 3/8" or 1/2" hole drilled into top of plastic box where power was taken. (Didn't go through the factory clamp.) Article 110.3.B

Hole in cabinet through wood and sheetrock into KO in box, no bushing or clamp. Article 317

Ground in "supply" box was was just lightly hooked around the grounds that were there. Can't think of which article applies here.

Did I miss anything? Do you agree/disagree?



I agree with everything, and 250.4 (a) (5) is the violation on the EGC's being lightly hooked
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I was running a switchleg for an exhaust fan in a house the other day and came across a receptacle in the kitchen cabinet for the microwave. GC stuck his head up and says, "Everything okay with that?" Didn't think to take a picture, but, here's what I observed:

The receptacle had no faceplate. Article 404.9.A

I agree it needs a cover.

It was wired with #14 off a 20 amp SABC. Articles 210.19.A.1, 210.19.A.3, 210.23.A.2, 240.4.D.3

Agreed. Having said that, it is not all that unusual for many electricians to claim this is OK.

Small 3/8" or 1/2" hole drilled into top of plastic box where power was taken. (Didn't go through the factory clamp.) Article 110.3.B
Not sure that the cable is required to go through the factory hole. But it does need to have some kind of clamp there.

Hole in cabinet through wood and sheetrock into KO in box, no bushing or clamp. Article 317
Cable has to be secured when entering box.

Ground in "supply" box was was just lightly hooked around the grounds that were there. Can't think of which article applies here.
Depends. Might be OK, might not be a proper connection. I am inclined to think your evaluation of it being inadequate is probably correct.

Did I miss anything? Do you agree/disagree?

It does not seem like this would be real hard to have done correctly in the first place.
 

Chamuit

Grumpy Old Man
Location
Texas
Occupation
Electrician
It does not seem like this would be real hard to have done correctly in the first place.

I learned later on in the day that the install was done by a sub-contractor for the company that sold the appliances in the kitchen. It was the only electrical work that had been done by them. And, not very well as you noted.
 