Had it been a 20 ft. cord instead of 150? Do you thin it would have tripped? just curious
Why would cord length make a difference?
Give the relative impedance of the person and the cord, I don't see the cord length making any difference.Had it been a 20 ft. cord instead of 150? Do you thin it would have tripped? just curious
I don't know why it makes a difference but I have seen gfi's not work on long extention cords several times in the past. I solved this problem by making a short corded recept. box with a gfci recept in it and solved the problem.
Gene...........
If the gfci was not grounded it only protects equipment. When properly gronde it will provide protection of people as well.
Gene
__________________________________________
Remember - Speed Kills and its not always you!
thats potentially dangerous (besides the possible issue of what box you put it in), and not osha compliant. Portable GFCIs need to have open neutral protection. Cant use a standard GFCI receptacle or deadfront to make a portable GFCI. Have to buy a commercial portable GFCI or use something like a hubbell GFM20
I really don't know why the GFCI at the supply end did not trip, but it was not because of the cord length. As a side note, not that makes any difference as to the GFCI tripping, given the fact that the metal housing of the saw was "hot", there had to be an open in the EGC at some point between the supply and the saw.The last case of a GFI not working was on a residental site where the temp. was about 250' away from the house. Three 100' cords run from he temp. into the house, 100' of 10ga, 2 - 100' 12ga. The plumber had and older sawsall with the metal housing laying on the damp concrete floor. kneeling beside a lavatory install he reached for the saw and it bit him. A quick check with the meter showed between 12 and 18 volts to the concrete floor depending on dampness (damp to film of water on floor). Gfi at the temp tested good, each cord tested good individually, but the three strung together would not make the gfi trip. yes it was a faulty sawsall. When grabbed by the plastic handle or the rubber boot it did not shock (naturally), but if you or it were in the damp locations it would shock you when you touched the metal part of the motor housing.
I made a quick gfi j-box with a bell box, a gfi recept., a weather proof cover plate, and a 3 wire pig tail (I carry them on my truck for disposal installs) and plugged it into the end of the cords and the sawsall into it. If someone grabbed the saw by the housing it tripped the gfi at the j-box every time if they were in concact with the damp floor as plumbers usually are.
The plumber quit cussing, except when the gfi tripped, and I went back to work.
Gene
Remember - Speed Kills and its not always you.
In the case of the saw, there are differences in the trip times of GFCIs, it could very well be that the only reason that the first one did not trip before the plumber let go of it was a longer trip time and the one from your truck had a shorter trip time.
091228-0823 EST
Busman:
See page 4 and Average Trip Time vs Fault Current curve on the datasheet at
http://www.national.com/ds/LM/LM1851.pdf#page=1&search="Ground Fault Interrupter%22
The UL spec maximum is about 6.5 sec at 5 MA from this plot. National's typical time is about 0.4 sec.