Brother just called, he got shocked by a drop cord on a GFCI

Status
Not open for further replies.

busman

Senior Member
Location
Northern Virginia
Occupation
Master Electrician / Electrical Engineer
That's interesting. I guess I'll have to get a precision 24 kOhm resistor and try it out.

Thanks,

Mark
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
091228-0942 EST

Busman:

With 25.5 K a sample Leviton does not trip in many seconds. With 20.5 K the trip time was maybe 0.5 to 1 second.

.
I think the standard permits a "no trip" if the fault current is less than 6mA and requires a "no trip" with the fault less than 4mA. With the 20.5 K load, the standard would permit a trip time of up to 5.78 seconds, but would also permit a "no trip".
 

busman

Senior Member
Location
Northern Virginia
Occupation
Master Electrician / Electrical Engineer
I was basing my experience on the GFCI test button on my fluke T+ Pro which has the following rating:

GFCI Test current
100 V - 150 V @ 6 mA - 9 mA ac, 150 V - 240 V < 12 mA
and it trips any GFCI I ever stuck it in so fast that it seems instantaneous. More research may be required.

Mark
 

480sparky

Senior Member
Location
Iowegia
you're joking, right??...........


No, he's not. GFIs cannot tell the difference between a load (a toaster, a night light, a cell-phone charger, whatever) between the hot and neutral and a human body between the hot and neutral. It sees both as a normal load.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
you're joking, right??

and..
GFCI's do not prevent shocks, they merely limit the duration of a shock.
No I am not joking....the shock has to happen before the GFCI acts. It does not prevent the shock...it limits it to a time that will not cause serious harm to most people.
 