I would get an extra level of comfort if I could visably see they were open. Voltage check is still required.
NFPA 70E
ARTICLE 120 Establishing an Electrically Safe Work Condition
120.1 Process of Achieving an Electrically Safe Work Condition.
An electrically safe work condition shall be achieved when performed in accordance with the procedures of
120.2 and verified by the following process:
(1) Determine all possible sources of electrical supply to the specific equipment. Check applicable up-to-date drawings, diagrams, and identification tags.
(2) After properly interrupting the load current, open the disconnecting device(s) for each source.
(3) Wherever possible,
visually verify that all blades of the disconnecting devices are fully open or that drawout-type circuit breakers are withdrawn to the fully disconnected position.
(4) Apply lockout/tagout devices in accordance with a documented and established policy.
(5) Use an adequately rated voltage detector to test each phase conductor or circuit part to verify they are deenergized. Test each phase conductor or circuit part both phase-to-phase and phase-to-ground. Before and after each test, determine that the voltage detector is operating satisfactorily.
(6) Where the possibility of induced voltages or stored electrical energy exists, ground the phase conductors or circuit parts before touching them. Where it could be reasonably anticipated that the conductors or circuit parts being deenergized could contact other exposed energized conductors or circuit parts, apply ground connecting devices rated for the available fault duty.