We've been running miles of Vitalink MC Cable for fire alarm and fire pump power. I've been told that according to the instructions you can space the cables like shown in the photo. I'm wondering, how this does not cause heating the surrounding ferrous metal by induction? Where is enters the steel enclosures a slot is cut between the individual KO's that complies with 300.20(B). Is it that a ferrous strut and strap about every 5' surrounding the cable is too small to cause any inductive heating?