These two and a half questions came up following work with some dead break connectors. Scroll down to page 3 of the product link for a useful cut-away that shows the plug inserted.
We completed the work and I was left with one of the insulating plugs shown in this image. My understanding is that this acts as a capacitor, with the threads and stud being plates and the plug body the die-electric.
My fluke 376's capacity mode does not read anything across it. The lowest that this meter can read reliably is 1 µF according to the fluke datasheet. I assume the value would be lower than that, but I rarely if ever touch capacitors that are not on a board.
Question 1: What test equipment could I use to check the capacity?
Eaton states that the voltage on a capacitive test point is 10-12% of line-to-ground voltage. For a 7,976V-Ground system, that would be ~798 to 957V. I'm going to use 850V.
My thinking would be that all is needed is the current through the connection at the time of measurement and the capacitive reactance of the plug, assuming the capacitance can be found. But I clearly have a misconception:
Vdrop= I * Xc ← Vdrop across the insulating plug AKA the capacitor.
Vdrop = I * (1/(2πfC)
Solving for C:
C=((Vdrop/I)-1)/2πf
Plugging in 850V for Vdrop, 50A for current, and 60Hz for freq:
C=22.17 Farads, which I assume is incorrect.
Question 2: how would, or can one calculate an expected voltage from test point to ground if measured at the insulating plug test point?
Question 2a: how would, or can one calculate the capacity of the plug?
This is a theory only. I can't think of a reasonable situation where an electrician would put a multi-meter on a 25kV test point to measure the potential to ground.
We completed the work and I was left with one of the insulating plugs shown in this image. My understanding is that this acts as a capacitor, with the threads and stud being plates and the plug body the die-electric.
My fluke 376's capacity mode does not read anything across it. The lowest that this meter can read reliably is 1 µF according to the fluke datasheet. I assume the value would be lower than that, but I rarely if ever touch capacitors that are not on a board.
Question 1: What test equipment could I use to check the capacity?
Eaton states that the voltage on a capacitive test point is 10-12% of line-to-ground voltage. For a 7,976V-Ground system, that would be ~798 to 957V. I'm going to use 850V.
My thinking would be that all is needed is the current through the connection at the time of measurement and the capacitive reactance of the plug, assuming the capacitance can be found. But I clearly have a misconception:
Vdrop= I * Xc ← Vdrop across the insulating plug AKA the capacitor.
Vdrop = I * (1/(2πfC)
Solving for C:
C=((Vdrop/I)-1)/2πf
Plugging in 850V for Vdrop, 50A for current, and 60Hz for freq:
C=22.17 Farads, which I assume is incorrect.
Question 2: how would, or can one calculate an expected voltage from test point to ground if measured at the insulating plug test point?
Question 2a: how would, or can one calculate the capacity of the plug?
This is a theory only. I can't think of a reasonable situation where an electrician would put a multi-meter on a 25kV test point to measure the potential to ground.