On a service call at a friends home for dimming lights and malfunctioning appliances I found the voltage at the service jumping all over the place. I used a voltage meter from hot to neutral. I found it as high as 125V and as low as 108V. I did not simultaneously measure both hots to neutral, but I think as one went higher the other went lower. When I measured both hots the voltage seemed more stable, staying right around 233V. These measurements were made on the bus after the meter and before the Main breaker. All exposed parts look clean, relatively new and free from corrosion.
I advised the HO to call POCO. From reading other threads here, I suspect a loose connection before entering the house.
Does that make sense that one phase drops while the other spikes?
Is there anything else I could have done for them?
I advised the HO to call POCO. From reading other threads here, I suspect a loose connection before entering the house.
Does that make sense that one phase drops while the other spikes?
Is there anything else I could have done for them?