So I'm working on an estimate for a detached garage and a generator that are approx. 200 ft. away from the main panel in a home.
I start doing the voltage drop calc for the garage at 80% of125Amps (max size snap in GE breaker available) at 240 volts and then I plug in 80% of 125 amps at 120 volts and it's a big difference. So I say to myself, ok so it's based on actual load. But we have no def loads at the time of building. (Basics welder, compressor, lift, etc.)
So I'm thinking I should plan for worst case scenario and size for the 120 volt calc. 4/0 Al URD.
What do you folks do?
So I'm working on an estimate for a detached garage and a generator that are approx. 200 ft. away from the main panel in a home.
I start doing the voltage drop calc for the garage at 80% of125Amps (max size snap in GE breaker available) at 240 volts and then I plug in 80% of 125 amps at 120 volts and it's a big difference. So I say to myself, ok so it's based on actual load. But we have no def loads at the time of building. (Basics welder, compressor, lift, etc.)
So I'm thinking I should plan for worst case scenario and size for the 120 volt calc. 4/0 Al URD.
What do you folks do?