Hello to all you experienced people out there!!!!
Heres what I've got. 1 20 amp lighting circuit in a commercial kitchen, overhead flourescent lighting. The Home run is about 200-225 feet long. The voltage at the panel is 117, The voltage at the destination is about 107.
The problem is flickering lights. Obvious what the problem is right? Well, I suggested reconnecting home run to 277v panel, since the ballasts are rated 120-277v. I am sure this will eliminate the flickering problem. But my dilemma
is this. Does code require a maximum voltage for this situation, Kitchen areas? Would I be using 277v in an environment that does not permit it? The 12 gauge copper wiring would still be permitted, therefore I would not have to change out the existing home run, right? Thanks, OLD MAN mefalk55
Heres what I've got. 1 20 amp lighting circuit in a commercial kitchen, overhead flourescent lighting. The Home run is about 200-225 feet long. The voltage at the panel is 117, The voltage at the destination is about 107.
The problem is flickering lights. Obvious what the problem is right? Well, I suggested reconnecting home run to 277v panel, since the ballasts are rated 120-277v. I am sure this will eliminate the flickering problem. But my dilemma
is this. Does code require a maximum voltage for this situation, Kitchen areas? Would I be using 277v in an environment that does not permit it? The 12 gauge copper wiring would still be permitted, therefore I would not have to change out the existing home run, right? Thanks, OLD MAN mefalk55