Very important concern, however, it hasn’t been addressed despite the responses.
Since you are asking how to calculate the current draw, perhaps you can go down to basics.
If doubts still persist the following will at least something to work on.
Ohm's Law is your friend.
You know the voltage. Put the VA rating aside for now, since that is what you are not sure (ie.doubtful) of its size.
Take the resistance of the magnet coil.
Ohm's Law:
E=IR
I= E/R
Value of I based on nameplate is 300 VA divided by 120 vac. = 300/120= 2.5A
Your coil resistance based on reading from your meter is X
From what are known:
R=120/I
2.5=120/R
Therefore:
R=120/2.5=
48 Ohms
Any value
lower than 48 ohms (from your meter) would require a larger transformer VA rating. You can increase the VA as a safety factor.
Easy peazzy
Physics can sometimes save you from falling into a deep precipice. How’s that for a metaphor.
.
Enlarging the control transformer is easier than adding those relays. . . and it also keeps the original concept.
Purists will argue:
But. we are talking about AC.
Well, you won’t be far off if you use the example above.
[/QUOTE
Myspark, did you mean to say "Any value
HIGHER than 48 ohms (from your meter) would require a larger transformer VA rating"?
Thanks, Isaiah