hardworkingstiff
- Wilmington, NC
In order to keep away from a disucssion of the "correct" voltage drop formula, for the sake of this topic, can we just assume that VD=IR?
On a 120-volt circuit, a 50-amp load 100' one way on a #4 wire should be 3.08-volts. ((100*2)*(.308/1000)*50). This is a 2.57% VD.
Make this 2 circuits that each pull 50-amps and wire them to a shared neutral conductor (single-phase 120/240-volt) and the voltage drop will still be 3.08-volts, but since it is shared across the 2 circuits which have an applied voltage of 240-volts, the voltage drop would be 1.28% instead of 2.57%.
Now let's say this same MWBC is connected to a 120/208 3-phase panel. If only one circuit is loaded, then the voltage drop would be the same as the 1st scenario (2.57%). Now, when you load up both circuits, the voltage drop will not be halved (as a %) since the neutral is carrying the same current as the other two ungrounded conductors.
I know I asked this before, but I'm not convinced the answer was ever really given. What is the VD on the second scenario when each (2) circuit is pulling 50-amps? How did you calculate that?
Thanks,
Lou
Thanks,
Lou