Essentially, what's needed is a definition of "design load" for general purpose receptacles, something that inherently has no design load.

As I had pointed out above, the worst case assumption for general receptacles is rather impractical in the real world and some sort of a compromise is needed that embodies the spirit of the requirement, say a maximum VD of 3% at 150 ft, which could easily be tested for during site inspections. This requirement makes the reasonable (IMHO) assumption that although some circuits would exceed 3% VD at the farthest receptacle, many other general purpose receptacle circuits would be loaded quite lightly, well below the 3% VD level, so that on average, considering many such circuits, the 3% requirement would be met.
This would certainly serve the Energy Efficiency intent of the Code.

Heinz R.

Agreed, well said.
 
Just to keep you folks informed on where this going. I'm in the process of Petitioning the Florida Building Commission for a "Declaratory Statement," essentially a formal interpretation of the meaning of "design load" for general purpose receptacles in the context of Chapter 13, Energy efficiency, in the Florida building code. This will take at least a couple of months and probably more.
I'll get back here when I have the Dec. Statement in hand.
In the meantime, thanks for everybody's thoughtful response.