Essentially, what's needed is a definition of "design load" for general purpose receptacles, something that inherently has no design load.
As I had pointed out above, the worst case assumption for general receptacles is rather impractical in the real world and some sort of a compromise is needed that embodies the spirit of the requirement, say a maximum VD of 3% at 150 ft, which could easily be tested for during site inspections. This requirement makes the reasonable (IMHO) assumption that although some circuits would exceed 3% VD at the farthest receptacle, many other general purpose receptacle circuits would be loaded quite lightly, well below the 3% VD level, so that on average, considering many such circuits, the 3% requirement would be met.
This would certainly serve the Energy Efficiency intent of the Code.
Heinz R.
Agreed, well said.