ok. Let's say :
I have a 300' lighting run, that's 277v 20a. I would need to run a #8 Cu THHN. With a 2.9% VD. If I ran a #12 the maximum distance I could run while staying within the 3% would be 121'. Question 1 : For a 300' run can i change to #12 from #8 at 179' and still have a 2.9%??
Question 2 :
The EGC. T250.122 lists 20A to be protected by a #12. With voltage drop coming into play and needing to upsize to #8, 250.122 (B) says I need to also increase the size of the EGC. If I used my conduit system (EMT) as my EGC, I bond to my junction box where I make my transition. Is there a size limitation for using my conduit system as my EGC relating to my ungrounded conductors???
I have a 300' lighting run, that's 277v 20a. I would need to run a #8 Cu THHN. With a 2.9% VD. If I ran a #12 the maximum distance I could run while staying within the 3% would be 121'. Question 1 : For a 300' run can i change to #12 from #8 at 179' and still have a 2.9%??
Question 2 :
The EGC. T250.122 lists 20A to be protected by a #12. With voltage drop coming into play and needing to upsize to #8, 250.122 (B) says I need to also increase the size of the EGC. If I used my conduit system (EMT) as my EGC, I bond to my junction box where I make my transition. Is there a size limitation for using my conduit system as my EGC relating to my ungrounded conductors???