ron said:Metallic conduit or raceway does not cause voltage drop.
It does so by hindering the dissipation of I^2R heat when compared to like conductors handling the same amount of current while suspended in free air.drivetr. said:How does a metallic conduit or raceway cause a voltage drop?
Smart $ said:It does so by hindering the dissipation of I^2R heat when compared to like conductors handling the same amount of current while suspended in free air.
Hindering heat dissipation is the major contributor to voltage drop for any type of conduit. Other differences, such as capacitive coupling, are quite small by comparison.sparkie001 said:Hindering the dissipation of heat will indeed raise the temp of the conductors, which will increase the resistance a bit, but his question was specific to metallic conduits, not conduits in general.
It would have helped if you had mentioned ["30%" or poor] PF?power factor?in your first post. Reactance is generally not an issue in the typical voltage drop questions I've seen posted here. Perhaps this thread may help. Post again if you have any further questions.drivetr. said:I'm referring to Chapter 9, Table 9. I read an article referring to Section 695.7 of the NEC and the author uses Table 9 in calculating voltage drop. He calculates the voltage drop of 500 feet, #700, @ 30% PF in steel conduit. Installing conductors in metalic conduit changes the reactance of the circuit.
drivetr. said:Why is there two rows per wire size? Table 8 has two rows up to and including #8; due to either stranded or solid wire. Why are two rows present for each conductor in Table 9?
drivetr. said:I believe (and I might be wrong) because when a conductor is placed in a metallic raceway, the reactance (specifically the inductive reactance) of the conductor increases. This increase in reactance causes a greater voltage drop (again, not by much but that depends on the material, length, etc.) because the resistance of the conductor increases.
Look at the top of table 9. The top number is ohms to neutral per kilometer, the bottom number is ohms to neutral per kilofoot.drivetr. said:Why is there two rows per wire size? Table 8 has two rows up to and including #8; due to either stranded or solid wire. Why are two rows present for each conductor in Table 9?
Also, does anyone know of an easy method to use Note 2 of Table 9?
I admit heat is not the issue as far as the OP is concerned. But while we're on the subject, I noticed Jon, too, mentioned heating in one of his posts. This leads me to the question I've often wondered about, never ran across any details, and never asked... Why are the resistance/impedance tables given at 75?C. Is this the temperature of the wire? ...ambient temperature inside the conduit? ...outside the conduit? ...the conduit, too? In many cases we are simply not permitted to have operating circuits at this temperature for any length of time. If this is meant to project worst-case scenario, is there an accepted method for adjusting to nominal operating parameters?beanland said:Heat is not the issue.
These statements are completely unsubstantiated. The fact is, in many but not all cases, the impedance is lowered. Please review the table at the following link: Customized Table 9. The .htm file was generated in Excel, so it will import quite well back into Excel. (The process may work better if you right click on the download link on the second page and choose "Save Target As" in the local menu; additionally, does anyone know of a better, non-image, free file host?)beanland said:Steel conduit raises the impedance of the set of conductors. The higher inductance (not resistance) increases voltage drop.