I can't vouch for any of these, I just went looking and that's what I came up with.Smart $ said:(additionally, does anyone know of a better, non-image, free file host?)
I can't vouch for any of these, I just went looking and that's what I came up with.Smart $ said:(additionally, does anyone know of a better, non-image, free file host?)
Where's the adjustment for inductance? Yes, it would be nice to pin all circuits down to a .85 PF. In the real world, it is only occasionally so.Rockyd said:In regard to voltage drop, at a reasonable PF (85%) we can use the following information...
Smart $ said:I admit heat is not the issue as far as the OP is concerned. But while we're on the subject, I noticed Jon, too, mentioned heating in one of his posts. This leads me to the question I've often wondered about, never ran across any details, and never asked... Why are the resistance/impedance tables given at 75?C. Is this the temperature of the wire? ...ambient temperature inside the conduit? ...outside the conduit? ...the conduit, too? host?)
I assumed that also.winnie said:I am pretty certain that the 75C is the conductor temperature.
I was aware of that formula... but how does one determine T2. Say, for example, we know the following parameters of a circuit:winnie said:See the note at the bottom of table 8 for temperature change; that is the standard formula used calculating resistance assuming a linear change in resistance versus temperature.
Smart $ said:..how does one determine T2.
You have pretty much confirmed my suspicions.winnie said:I'm pretty sure that T2 is the actual conductor temperature at which you are trying to calculate voltage drop, not the allowed temperature rise...
Unfortunately there is no easy way to calculate T2 in normal situations, since it requires knowledge of the thermal conductivity between conductor and ambient; for a given current flowing through the wire in a given ambient temperature, the wire sitting in 'free air' will be much cooler than the wire buried in thermal insulation. Table 310.16 makes certain assumptions about the thermal resistance to ambient, IMHO pretty conservative estimates.
If you want to calculate T2 using the same thermal resistance assumptions as table 310.16...
Not sure if you are aware of it, but Table 9 lists circuits in PVC as having inductive reactance (#10Cu XL = 0.050Ω/1000'), same column as Aluminum Conduit. The use of PF = 1 does negate any effect it has on the circuit.ramsy said:I agree checking the rise with a calc beats assumptions.
11.42 = Temp. rise 60c, Steel conduit, PF=0.8 (Error if over 60c)
11.97 = Default 75c, Steel conduit, PF=0.8
14.40 = Default 75c, PVC conduit, PF=1
I'm inclined to go with the latter. However, without empirical evidence to back that conclusion up, I'm afraid it is but mere speculation on my part. Did you notice I used a derated I@max?C of 32, because of the 6 ccc's in the conduit? Do you not consider this a logical assumption?ramsy said:If derating #10 permits the 24A load, can we do it this way?
T2 = Ambient + (Load / I@MaxC * 60c )
T2 = 30 + 24 / 40 * 60 = 66c
Or, is it this way:
T2 = Ambient + (Load^2 / I@MaxC^2 * 60c )
T2 = 30 + 24^2 / 40^2 * 60 = 52c
Smart $ said:Not sure if you are aware of it, but Table 9 lists circuits in PVC as having inductive reactance..
Smart $ said:I'm inclined to go with the latter. However, without empirical evidence to back that conclusion up, I'm afraid it is but mere speculation on my part.
Smart $ said:Did you notice I used a derated I@max?C of 32, because of the 6 ccc's in the conduit? Do you not consider this a logical assumption?
In reality, the 14.40 VD would only match a DC circuit, and only under a completely different and unique set of circumstances than the example. But there are many that consider such a valid voltage drop calculation result for an AC circuit!ramsy said:Yuk, didn't see that before. Perhaps 14.40 matches only for voltages below 600vac.
So Load^2 / I@max?C^2 it is.ramsy said:I don't have a white book either. However, Google searches showing IEE references related to Temp.rise are using load^2 / I@MaxC^2 in the equation. See near bottom page.
http://www.cda.org.uk/megab2/elecapps/pub116/appen32.htm
First off, I only have (8) #10 AWG conductors in the 1" EMT. I said the example circuit is an L-N circuit in one of two 4-wire MWBC's. That's two "edisons", "full boats", or A,B,C,N sets. Assuming linear loads (i.e. not non-linear), only the line conductors count as current carrying conductors, of which there are six (6), and thus they are derated from 40 to an ampacity of 32.ramsy said:NEC 310.15 tables don't show your 12 conductor factor of 0.7 affecting the temperature, perhaps my brain isn't flexing enough to translate this for T2, but building a derating limit for ampacity into T2 is not a bad idea. I'm just used to doing that seperately.
Smart $ said:..more heat is retained in the conductor, causing the conductor to reach max?C at a lower amperage. It only seems logical to me to use the derated ampacity as the current which corresponds to max?C. To use any other more precise method would require usage of the formula in 310.15(C).