The footnote to table 250.122 has been changed in the 1999 and 2002 NEC
It used to say may need to be
Now it states shall be
There are times when 250.122 results in an undersized EGC. We all know to upsize the EGC for voltage drop.
There is a free software program "GEMI" available at Mikes website, that allows one to calculate the max length of rigid for a circuit and when a supplemental EGC is required. Its based on studies done at the University of Georgia.
Based on my use of the program, rigid conduit typically needs an EGC starting when its over a 300 ft run.
It used to say may need to be
Now it states shall be
There are times when 250.122 results in an undersized EGC. We all know to upsize the EGC for voltage drop.
There is a free software program "GEMI" available at Mikes website, that allows one to calculate the max length of rigid for a circuit and when a supplemental EGC is required. Its based on studies done at the University of Georgia.
Based on my use of the program, rigid conduit typically needs an EGC starting when its over a 300 ft run.