Voltage drop and Transformer calculations
zcanyonboltz
denver
I'm studying to take the master electrician exam already hold my RW and journeyman it's been awhile since I've done voltage drop calculations and Transformer are there examples in Annex d or chapter 9 examples of voltage drop and or Transformer calculations just something I can refer to when taking the exam so I don't have to study for it that hard I know there's only a total of 2 questions each on the exam thank you
I've been studying this a bit can anyone tell me where the 12.9 ohms value for K copper and the 21.20 ohms value for K aluminum come from are those values in the NEC? Thanks
I've been studying this a bit can anyone tell me where the 12.9 ohms value for K copper and the 21.20 ohms value for K aluminum come from.
They are physical properties of the metals and I believe they were derived via experimentation.
Thank you it's pretty simple just been a long time since I was in first year apprenticeship school easier to just learn how to do rather than having to look for an example which I haven't found in chapter 9 or the annex
2xKxIxD÷VD I just couldn't remember where K came from but it all the textbook examples I found those numbers are staying constant thank you
FWIW, if you look at Table 8 in Chapter 9 at ohms per k ft for 1000 kcmil AL & Cu you will find those numbers.
Hey remember this. 75 is passing. Once you pass, it will never matter that someone else whatever. EVERY calculation question takes time and there is always a higher risk that you will make a math error. So, set those aside and also set aside those questions that you can't locate quickly in the code book. Do those last.
So if I'm given a question does the value for K stay at 12.90 ohms for copper and 21.20 ohms for aluminum or can those values change?
I believe those numbers are based on a conductor temperature of 75°C. That is also the temperature the values in the Chapter 9 tables are based on.