I am using the formulas D=(VD*CM)/(1.732*K*I) to calcualte the maximum distance due to a specific voltage drop for a 1800W electrical equipment 120/208V.
where D is the maximum distance
CM is the circular-mils
K is direct current constant, here using 12.9 for copper wire
I is the load curret
Assuming 2% of votage drop, VD is 208*2%=4.16V
Load current 1800/208/1.732=5A
For #6 AWG, CM=26240
Finally, I got the maximum distance D=977ft
What confusing me is that in the product spec, it only allows 557ft in this case, is that company wrong with this data?