I have an service application
275'
200 amps
240/120 Single phase
I do the math for feeders from the meter
2*275*21.4*200 / 7.2 volt (3% voltage drop on 240) = 326944
that said using table 8 c9 I need to use 350kcm al USD/USE
I was talking with the POCO and if we wanted the meter on the house it would still be a run of 275' but he would run 4/0 al
What did I miss????
275'
200 amps
240/120 Single phase
I do the math for feeders from the meter
2*275*21.4*200 / 7.2 volt (3% voltage drop on 240) = 326944
that said using table 8 c9 I need to use 350kcm al USD/USE
I was talking with the POCO and if we wanted the meter on the house it would still be a run of 275' but he would run 4/0 al
What did I miss????