Re: Voltage Drop Calcs
Ok
Tom Henry gives several formulas to cover pretty much anything you need to do with Voltage Drop
with these, he also provides a chart that lists the EXACT 'K' values for All wires, solid, stranded, copper, aluminum, coated or not from #14 to 1000 kcmil
These values range anywhere from 12.5598 to 12.9
The Formulas are as follows:
BTW: K is Exact K according to the chart
D is Distance
I is Amperes
CM is Circular Mils
(sorry if everyone already knows that)
To find Voltage Drop - VD = 2 x K x D x I divided by circular mils
To find Wire Size - CM = 2 x 12.9 x D x I divided by Voltage Drop permitted in Volts
To find Distance - D = CM x VD permitted divided by 2 x K x I
To find Load - L = CM x VD permitted divided by 2 x K x D
when I say Wire size, distance, or load, it is just a way of breaking the VD formula into different parts using different KNOWN factors..
Ideally, if you want to know what size wire you will need to pull 23 amps at 240 volts with a circuit length of 225 feet, you would use the second formula
if you wanted to know how far you could run a #10 copper wire with a load of 12 amps at 480 volts you would use the distance formula...
has anyone seen these formulas? they seem like they could be useful and time saving...
EXCEPT
I have found what I feel to be a LARGE error in the second formula, the one for wire size, as applies to the code requirements for Ampacity per 310.16
The Problem i have is that if you use the Wire Size formula to figure the Circular Mils required to handle a Load of 100 Amperes at 480 volts 3phase on a circuit 150 ft long, it tells you to use #6 wire..... now according to 310.16, #3 is the MINIMUM required for 100 amp load, not considering circuit length, or derating...
i know this has been an extensive post, but this is something that REALLY irritates me.
Tom Henry's course costs QUITE a bit of money, and when you call them and say, HEY!! your formula is USELESS! All they say is.... well you have to look at table 310.16....
well hell, thats where I STARTED!! Before I THOUGHT about VOLTAGE DROP!!!
does this make any sense to anyone but me??