Re: Voltage Drop Calcs
The formula for caculating DC resistance is:
R = (K/A) x 1000 ohms per 1000 ft.
R ohms per 1000 ft
K volume resistivity in ohms-cmil/ft
A cross setional area in cmil
Using the given resistance in table 8 you can determine the value of K. The value for #12 was 12.6 and for 4/0 it was 12.6. The value of K is at 75C. K = 10.57 at 25C. The value of K should remain fairly constant at any temperature.
I don't think the formula can be used with table 310.16. Voltage drop at any amperage varies with the distance. If the distance is 10 ft you may get an answer of #12 cu instead of #6.
[ April 16, 2005, 02:48 PM: Message edited by: bob ]