210313-1400 EST
Note: the original post was with a hair dryer, basically a resistance for the most part. Dsg319's results were generally correct, and more accurate instruments would likely have produced somewhat better results. Note: that he used a resistive load so that reactive loads are not of concern.
So I setup some crude experiments. The wire is Romex #14 copper of a nominal 50 foot roll. The room temperature loop resistance should be about 0.253 ohms from published wire tables.
With my General Radio LRC bridge I measured 0.242 ohms at DC, and 0.275 ohms at 1000 Hz. On the same bridge on low Q inductance I read 13.5 microhenrys at a low Q of 0.31 . This inductance at 60 Hz has an inductive reactance of about 0.005 ohms. Small compared to either AC or DC resistance measurements.
With a load current of 11.7 A thru the cable the voltage at the load end was 109.0 V and at the input end was 112.4 V, or a change of 3.4 V for the loop. Thus, the cable loop resistance calculates to 3.4/11.7 = 0.29 ohms. This is reasonably close to the 20 deg C table value of 2.53 ohms per 1000 ft. And because of the way the test was run there was some cable heating.
.