Karl H said:
I'm using VD=(1.732xKxIxD)/CMILS and I'm finding it too primative and incomplete without doing ambient correction adjustments.
3 phase VD = 1.73 x K x D x I/CMILS. Another formula you can use is
1.73 x Distance x R from table 9 x I /1000. WE use the 75C resistance from table 9.
From the table R 4/0 cu = 0.062/1000 ft.
VD = 1.73 x 850 ft x .0.062 x 250 amps/1000 = 22 volts.
This is usually close enough for your use.
 
Last edited:
Voltage drop on pole lights

Voltage drop on pole lights

This may be alittle off topic, but can anybody tell me if this is ok? I have 3 light poles that are 120 volt, each drawing about 4 amps, the 1st is 250' from panel, 2nd is bout 400' from panel, and last is about 650' from panel. Is #8 copper good enough with the voltage drop, mainly for that last one, they are actually spliced in a underground jbox about 200' from the panel. Thanks for any advice.
 