Voltage drop & conductor size

Merry Christmas

OK Sparky 93

Senior Member
Location
Iridea14Strat
Occupation
Electrician
I’m stretching here.

When it comes to Vd and wire size and distance, I want to play out a scenario. I don’t know actual distance, only guesstimating.

5HP motor 1 phase
21.9 nameplate amps
30.8 per table amps
Approximately 200ft
208 volt

Based on info #10 would only be good for about 115 feet.

There entire length would need #6. Another entity told customer they needed #8.

It currently has #10

The way I see it is at the least #6 would or could be installed to the point that the #10 could handle.
Does anyone see it differently? Would you see anyway #8 could be ran, unless the total distance is less than what I am estimating?

I don’t see the real need at this point to need to run #6 the entire distance. Just an intercept.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Guessing without any more info:

I would run something like #2 al from the source to the local panel or disconnect.

I prefer to land wires on terminals and avoid unnecessary splicing.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
It would probably take one of the engineering type here to provide a reliable answer as we are dealing with motor loads.
Based on the 22 amps running load your #10 would be sufficient (5% drop) but the #10 is likely not sufficient taking inrush current into account.

Looking at charts from some of the pump manufactures it appears the #10 max distance is 150 to 180 ft.
Based on that I would think a #8.
 
Last edited:

Knightryder12

Senior Member
Location
Clearwater, FL - USA
Occupation
Sr. Electrical Designer/Project Manager
From my calcs with the info provided #8 would give you a 3.9% VD and #6 would give you 2.4% VD. So if you are not worried about meeting the energy code #8 should be good.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Based on the 22 amps running load your #10 would be sufficient (5% drop) but the #10 is likely not sufficient taking inrush current into account.
Is there an accepted engineering standard for doing a motor inrush voltage drop check? I.e. what current to use (some multiple of the nameplate FLC?) and what voltage drop is allowable at that current?

Cheers, Wayne
 