Voltage drop & conductor size
OK Sparky 93
Iridea14Strat
I’m stretching here.
When it comes to Vd and wire size and distance, I want to play out a scenario. I don’t know actual distance, only guesstimating.
5HP motor 1 phase
21.9 nameplate amps
30.8 per table amps
Approximately 200ft
208 volt
Based on info #10 would only be good for about 115 feet.
There entire length would need #6. Another entity told customer they needed #8.
It currently has #10
The way I see it is at the least #6 would or could be installed to the point that the #10 could handle.
Does anyone see it differently? Would you see anyway #8 could be ran, unless the total distance is less than what I am estimating?
I don’t see the real need at this point to need to run #6 the entire distance. Just an intercept.
Guessing without any more info:
I would run something like #2 al from the source to the local panel or disconnect.
I prefer to land wires on terminals and avoid unnecessary splicing.
It would probably take one of the engineering type here to provide a reliable answer as we are dealing with motor loads.
Based on the 22 amps running load your #10 would be sufficient (5% drop) but the #10 is likely not sufficient taking inrush current into account.
Looking at charts from some of the pump manufactures it appears the #10 max distance is 150 to 180 ft.
Based on that I would think a #8.
From my calcs with the info provided #8 would give you a 3.9% VD and #6 would give you 2.4% VD. So if you are not worried about meeting the energy code #8 should be good.
Is there an accepted engineering standard for doing a motor inrush voltage drop check? I.e. what current to use (some multiple of the nameplate FLC?) and what voltage drop is allowable at that current?
Cheers, Wayne