Fellow electricians and engineers,
I’m designing a pathway lighting system for a residential estate using low-wattage (8W) 120V LED bollard fixtures, spaced ~20 ft apart along a 300-foot one-way run from the panel. Total load: 12 fixtures × 8W = 96W (~0.8A at 120V).
The fixtures are UL-listed, constant-voltage type (not Class 2), and specify an operating range of 105–130V.
My question centers on voltage drop:
Using 12 AWG THWN in PVC, the calculated voltage drop is ~2.1% (about 2.5V) at full load—well under the common 3% informal guideline.
However, I’ve heard conflicting opinions: “Since LEDs draw so little current, voltage drop isn’t a concern,” vs. “LED drivers can behave unpredictably below minimum voltage—even if power loss seems negligible.”
Does NEC provide any specific guidance for voltage drop with electronic LED loads?
I know NEC doesn’t mandate a max VD except in fine print notes (e.g., 210.19 FP Note 4, 215.2 FP Note 2), but from a performance and warranty standpoint, should we still enforce stricter limits for sensitive electronics?
Also: if the first fixture sees 119V and the last sees 116V, is that truly acceptable—even if within the manufacturer’s spec? Could it cause flicker, reduced lifespan, or color shift over time?
I’m designing a pathway lighting system for a residential estate using low-wattage (8W) 120V LED bollard fixtures, spaced ~20 ft apart along a 300-foot one-way run from the panel. Total load: 12 fixtures × 8W = 96W (~0.8A at 120V).
The fixtures are UL-listed, constant-voltage type (not Class 2), and specify an operating range of 105–130V.
My question centers on voltage drop:
Using 12 AWG THWN in PVC, the calculated voltage drop is ~2.1% (about 2.5V) at full load—well under the common 3% informal guideline.
However, I’ve heard conflicting opinions: “Since LEDs draw so little current, voltage drop isn’t a concern,” vs. “LED drivers can behave unpredictably below minimum voltage—even if power loss seems negligible.”
Does NEC provide any specific guidance for voltage drop with electronic LED loads?
I know NEC doesn’t mandate a max VD except in fine print notes (e.g., 210.19 FP Note 4, 215.2 FP Note 2), but from a performance and warranty standpoint, should we still enforce stricter limits for sensitive electronics?
Also: if the first fixture sees 119V and the last sees 116V, is that truly acceptable—even if within the manufacturer’s spec? Could it cause flicker, reduced lifespan, or color shift over time?