Voltage drop for 24 VDC Estop circuit

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
I’ve got an ESTOP circuit that runs about 1400 feet total and has three locations along its path - all switches are in series.
The switches are fed off an Allen Bradley 440R relay. I’m assuming since this is a simple open/close scenario there is little (or no) amp draw and voltage calc should be determined by cable resistance only - in this case pair #16AWG. Am I on the right track?


Sent from my iPhone using Tapatalk
 
If these are going to a monitored estop relay, it uses pulses of 24 vdc to make sure there are no cross channel shorts.

Fourteen hundred feet is a long way to run wires with square wave pulses in them.
 
If these are going to a monitored estop relay, it uses pulses of 24 vdc to make sure there are no cross channel shorts.

Fourteen hundred feet is a long way to run wires with square wave pulses in them.

Thanks petersonra. Would you happen to have a sample calculation assuming these are monitored?