Voltage drop for 24 VDC Estop circuit
Isaiah
Baton Rouge
Electrical Inspector
I’ve got an ESTOP circuit that runs about 1400 feet total and has three locations along its path - all switches are in series.
The switches are fed off an Allen Bradley 440R relay. I’m assuming since this is a simple open/close scenario there is little (or no) amp draw and voltage calc should be determined by cable resistance only - in this case pair #16AWG. Am I on the right track?
While 16 AWG might work, suggest running 14 or 12 AWG, stronger for pulling. Of course assuming stranded and the e stops will take a 14 or 12.
If these are going to a monitored estop relay, it uses pulses of 24 vdc to make sure there are no cross channel shorts.
Fourteen hundred feet is a long way to run wires with square wave pulses in them.
Thanks petersonra. Would you happen to have a sample calculation assuming these are monitored?
Nope. I have no idea how warped the square wave would be after 1400 feet, nor what tolerances the relay would accept for square wave degradation.