ramsy
NoFixNoPay Electric
- LA basin, CA
- Service Electrician
A 1-PH x 3 cord to 5-prong, 3-PH plug, or "X" adapter would balance nicely, but Hubbel may have missed it. When using 208Y/120 with "Y" adapters (attached below), that extra phase does seem odd mixing with the next receptical or slip.
About this 44A neutral vector, it seems to deal more with power than current-interference in the nuetral, or the 0.866 resistance-demand factor applied to 3-PH voltage drop. See attachment, and the brief discussion last April.
This 0.866 voltage-drop-resistance factor for 3-PH current, included with Z based on NEC Tbl.9, along with 2x distance conversions is a 1.732 total 3-PH adjustment in my model, and has so far matched your VD results when using the same numbers. We might be using the same proprietary model, which address everything but segment-interference magnitudes.
We havn't agreed on neutral current yet, which alters VD across this segments, but as Smart noted with these dynamic loads, it really shouldn't matter if neutrals are sized for worst-case scenarios near 50 amps.
Also the way I tried to add those segments before was incorrect. Saw multiple loads adding current in parrallel, but this is the same load just changing magnitude with interference and resistence in the neutral.
Without fixed loads between phases, and fixed current-interferance magnitudes, I believe one maximum-current value should be used to calculate VD for the entire length.