I am calculating voltage drop for an overhead crane. 3 phase 480 total length from source including conductive rails and traveling cable to the furthest point is 600 feet. When I run the numbers for voltage drop based on the overcurrent device <50 amp breaker> I am getting a #3 to be within 3% however when I use the total FLA of the 3 motors <19 amps> I am figuring a #6.
Is it acceptable to use the combined FLA when calculating VD for a motor load circuit or do I need to consider the starting current?
The formula I am using is 1.732*K*D*I/cm
I must back up my numbers with the government before they will accept the crane installation.