YouConduit!
Member
- Location
- Midwest
- Occupation
- Electrical Design
Dealing with a remote location where the 120/240V, 1-phase, 100A distribution panelboard is ~300 feet away from the utility meter. This is a 100A service.
All of the loads are very robust equipment with nominal voltage ranges of 200-250VAC for the 240V loads and 100-130VAC for the 120V loads. Load calcs add up to 8kVA. Typical usage is <1/2 of that.
What size should the service conductors be? Without considering voltage drop, I would say CU #2s. Should the cables be upsized for voltage drop if all of the equipment is manufactured for a broad range of voltages (well below what it should ever see)?
All of the loads are very robust equipment with nominal voltage ranges of 200-250VAC for the 240V loads and 100-130VAC for the 120V loads. Load calcs add up to 8kVA. Typical usage is <1/2 of that.
What size should the service conductors be? Without considering voltage drop, I would say CU #2s. Should the cables be upsized for voltage drop if all of the equipment is manufactured for a broad range of voltages (well below what it should ever see)?