brother
Senior Member
why are there so many different formulas for voltage drop? Ive been brushing up on some of my calcs and when I first started out I do not recall so many forumlas. Which ones do you use?? I think that the uglys book is the most simple and easy to remember, they have a standard 12.9 for copper and 21.9 for aluminum. these other formulas you have look up and they tend to vary.
vd= (2 x R x L x I)/1000 single phase
vd= [(2 x R x L x I)/1000] x .866 3 phase
uglys book formula
vd= (2 x K x I x D)/cm single phase
vd= (sqroot of 3, x K x I x D)/cm 3 phase
k=12.9 resistance for copper , k=21.9 for aluminum
vd= (2 x R x L x I)/1000 single phase
vd= [(2 x R x L x I)/1000] x .866 3 phase
uglys book formula
vd= (2 x K x I x D)/cm single phase
vd= (sqroot of 3, x K x I x D)/cm 3 phase
k=12.9 resistance for copper , k=21.9 for aluminum