Because of voltage drop my customer is suppliyng me with 1/0 cable from MCC to my skid edge for a motor heater 120/1ph/60hz/5.5A. Planning on terminating 1/0 wire in a junction box on a Power Distribution block and stepping wire down to a #6AWG. My question is for wire cost what is the smallest wire i can use instead of #6AWG for 25' run from the jucrion box to the motor heater without affecting the voltage drop?
 
Also... these numbers weren't making sense to me so I checked them. What percentage of VD are you wanting? Theoretically speaking even at a MILE (which would never be done lol) the VD on a 120V circuit with 5.5A and 1/0 CU conductors would only be about 5.9% on a resistive load. You can go 500' with #6's and only be at 2.25%. Something isn't adding up here.
 
Not only that, but for the cost of that 1/0 wire, why wouldn't you run a pair of 14ga wires at 480V out to a box next to the motor and put in a little 750VA transformer (assuming you can't change the heater voltage)?
 
VOLTAGE DROP

VOLTAGE DROP

Because of voltage drop my customer is suppliyng me with 1/0 cable from MCC to my skid edge for a motor heater 120/1ph/60hz/5.5A. Planning on terminating 1/0 wire in a junction box on a Power Distribution block and stepping wire down to a #6AWG. My question is for wire cost what is the smallest wire i can use instead of #6AWG for 25' run from the jucrion box to the motor heater without affecting the voltage drop?

I gave the wrong info. It's not a motor heater but a 525w Frame Space Heater but am still trying to use smallest wire possible out of my junction box and staying within a 5%VD. Will changing to a substantially smaller wire size at the junction box have any affect on the VD at such a shotr distance?
 
I gave the wrong info. It's not a motor heater but a 525w Frame Space Heater but am still trying to use smallest wire possible out of my junction box and staying within a 5%VD. Will changing to a substantially smaller wire size at the junction box have any affect on the VD at such a shotr distance?

How far away is the heater?
 
no issue
just wanted to make sure i wasnt going to affect the voltage changing to such a smaller wire size copmared to 1/0

Got it. Yeah, I'm not sure why anyone would think you would ever need 1/0's on a 120V, 525w load. You could go a little bit over 200' and still stay under 3% VD on that branch.
Are you absolutely sure you got all the numbers right (voltage/phase/wattage/etc.)? I'm only asking because I find it curious where the idea for the supplied 1/0's came from.
Just to maybe put this into perspective - Your standard residential portable space heater is typically about three times the load you've given us.
 
Got it. Yeah, I'm not sure why anyone would think you would ever need 1/0's on a 120V, 525w load. You could go a little bit over 200' and still stay under 3% VD on that branch.
Are you absolutely sure you got all the numbers right (voltage/phase/wattage/etc.)? I'm only asking because I find it curious where the idea for the supplied 1/0's came from.
Just to maybe put this into perspective - Your standard residential portable space heater is typically about three times the load you've given us.

Yes all correct, the customers MCC in the plant is a good distance from the motor skid since were operating in a hazardous area not exactly sure how far it is just that I need to provide for their 1/0 wire.
 
Is a bit odd. Sounds more like a install for a 10 rather than a 1/0 :)
 
.. what is the smallest wire i can use instead of #6AWG for 25' run from the junction box to the motor heater without affecting the voltage drop?

Ignoring feeders and assuming appropriate OCP is provided and copper conductors are used:

If you can keep the 1/0 portion to below 2835', your smallest wire would be a #18.
 
I agree with augie47, something is amiss here. 10ga instead of 1/0 sounds like a lot more possible scenario.

I can't imagine that connecting 1/0 cable to a little 525W heater is going to be even REMOTELY possible!
 
Yes all correct, the customers MCC in the plant is a good distance from the motor skid since were operating in a hazardous area not exactly sure how far it is just that I need to provide for their 1/0 wire.

Operating in a harzardous area?
a 120/1 20 A ckt from an MCC?

gotta be a closer source of power

what is motor skid?
and a frame heater?
 
If all this information you've given is actually true and accurate then your customer is grossly misinformed and you're enabling their ineptitude. This is a good example of when you shouldn't let a customer tell you how to do your job.