Happy Sunday evening everyone,
 I  have a voltage drop calculation question.
 I have 5 LED  208V 1 PH Area lights going to be installed in a  parking lot 100 ft. apart from each other, the 208V source also being 100 ft. from the first light pole.
 Each LED light draws 3 Amps.
 I plan on installing #6 Al USE, but not sure which end of the circuit to start the calculation.
Can someone show me the procedure and which end of the circuit to start on?
 Thanks in advance
Call the final fixture, fixture #1.
Call the fixture nearest the source, fixture#5.
Resistance from fixture 1 to 2 is R1.   Corresponding current is 1*I.  And the volts Voltage drop, I*R1.
Resistance from fixture 2 to 3 is R2.   Corresponding current is 2*I.  And the volts Voltage drop, 2*I*R2.
Resistance from fixture 3 to 4 is R3.   Corresponding current is 3*I.  And the volts Voltage drop, 3*I*R3.
Resistance from fixture 4 to 5 is R4.   Corresponding current is 4*I.  And the volts Voltage drop, 4*I*R4.
Resistance from fixture 5 to to the source is R5.   Corresponding current is 5*I.  And the volts Voltage drop, 5*I*R5.
Assuming that you've uniformly spaced each fixture according to circuit length, then all resistances are identical.   If not, they depend on length.
Rn = 2*r*Ln/(1000 ft/kft)
where
Rn is one of the above resistances, and n is the number 1 thru 5
r is the ohms/kft from the NEC.
Ln is the length of the portion of the circuit in particular.  You need to account for the total length of the circuit, and not just the line-of-sight distances.
Note that the factor of 2 applies for single phase and DC circuits.  If this is 3-phase, replace this with sqrt(3).
Add it up:
Vdroptotal = I*(R1 + 2*R2 + 3*R3 + 4*R4 + 5*R5)
Or, in terms of percentage:
%Vdroptotal = I*(R1 + 2*R2 + 3*R3 + 4*R4 + 5*R5)/Vnom
L1 thru L5 all equal 100 ft.  The resistance of #6 AL wire is r=0.808 ohms/kft.  Thus for single phase, each resistance Rn is 0.1616 Ohms.
%Vdroptotal = 3A*0.1616 Ohms *(1 + 2+ 3 + 4 + 5)/Vnom
%Vdroptotal = 3A*0.1616 Ohms *15/208V
%Vdroptotal = 3.5%