Deltaforce
- India
- Electrical Engineer
The key one based ohm law and other on circular mil formulaHow does the OP apply the equations he has? Under what circumstances? We can only guess these are not on an EE exam.
Yes, but tell him why he would use one versus the other. Twenty words or less that does not require an EE degree to understand.The key one based ohm law and other on circular mil formula
No, the opposite, and you get the same %Vd number either way. 2DIR/240V = DIR/120V, just like DIR(sqrt(3))/480V = DIR/277V.For 240v, you use one way resistance and 120v you use two way resistance, right?
For the balanced case with a neutral you only need Ohm's Law and the AC resistance of the conductors. The one way Vd in a single phase conductor compared to the phase to neutral voltage is the %Vd for the conductor set, whether it be single or three phase. Personally, when I can I would rather solve problems with first principles rather than by using formulas with derived constants in them.How does the OP apply the equations he has? Under what circumstances? We can only guess these are not on an EE exam.
To be clear, by the "balanced case" you must mean a 2-wire single phase or a balanced (equal current) 3-wire 3 phase circuit, and the "neutral" you refer to would be a possibly fictitious neutral that may not be present in the circuit. E.g. for a 2-wire 120V L-N circuit, your fictitious neutral would be 60V from each conductor, and then you could either use 60V and the one-way resistance, or 120V and the two way resistance. Since multiplication is commutative.For the balanced case with a neutral you only need Ohm's Law and the AC resistance of the conductors. The one way Vd in a single phase conductor compared to the phase to neutral voltage is the %Vd for the conductor set, whether it be single or three phase.
I believe all ggunn is saying is that if you have a 240V 2-wire load, and you want to compute the %Vd, you can use 240V along with the two-way resistance, or use 120V along with the one-way resistance. You'll get the same %Vd either way.But if 240v and 120v supply same power., current 240v system lower, voltage drop lower, but in 120v system, current higher, voltage drop higher. Then how %vd same in 240v and 120v?
Voltage drop for different voltages, load power to consider to find current. So current not same in two cases. See #27I believe all ggunn is saying is that if you have a 240V 2-wire load, and you want to compute the %Vd, you can use 240V along with the two-way resistance, or use 120V along with the one-way resistance. You'll get the same %Vd either way.
For absolute Vd, using 240V and two-way resistance gives you the absolute Vd between the 2 wires. And using 120V and the one-way resistance gives you the absolute Vd of one of the wires relative to a fixed neutral point. Which is just 1/2 of the absolute Vd between the 2 wires.
Cheers, Wayne
Yes, I don't believe that ggunn commented on that situation.Voltage drop for different voltages, load power to consider to find current. So current not same in two cases. See #27
Sorry, I misinterpreted your earlier question. For a 120V two wire run, yes, you use 2D.But if 240v and 120v supply same power., current 240v system lower, voltage drop lower, but in 120v system, current higher, voltage drop higher. Then how %vd same in 240v and 120v?
See my questions in the link, hopefully this helps.How does the OP apply the equations he has? Under what circumstances? We can only guess these are not on an EE exam.
Two decimal places seems extreme.See my questions in the link, hopefully this helps.
It's accurate for sizes smaller than 1/0, and accurate for DC. For sizes 1/0 and larger when used with AC, other factors come into play, and the conductance per unit length isn't perfectly proportional to the kcmil area of the wire. As a second order effect, larger wires increase the effective AC resistance, along with the raceway type, whether it's plastic, non-ferrous metal (e.g. aluminum and stainless), or ferrous metal (e.g. steel). It has to do with inductance and the skin effect.Hi all,
Thank you so much for the help with understanding. Knowing that the 2kid is more of the equation that represents the round trip of the wire length was helpful. I am going to continue only with the this equation for my tests. The other seems to basic for what the tests are inquiring about. Here are two pics of the Q&A of these tests. They are both single phase questions but are using different methods of solving. Again i am just going to use 2KID as it seems more accurate.
...was... ?Somewhat ironic this hasn't been posted after 35 posts but here is some background without getting too far into the weeds...
Mike Holt Enterprises - the leader in electrical training.
Mike Holt worked his way up through the electrical trade from apprentice electrician through electrical contractor, to become one of the most recognized experts in the world as it relates to electrical power installations. He was a Journeyman Electrician, Master Electrician, and Electrical...www.mikeholt.com
Mike Holt Enterprises - The leader in electrical training.
The more the merrier, thanks!Somewhat ironic this hasn't been posted after 35 posts but here is some background without getting too far into the weeds...
| X=2*pi*f*(0.1404*log10(2*S/dia)+0.0153)/10^3 [ ohm/1000ft] s=distance center-to-center |
Ohm's law still applies. Precision may not be as high with one method vs another. Commonly used in the field calculations assume a certain temperature (30C I believe) to come up with a factor that is kind of universally used to come up with the resistance portion in Ohm's law which is considered good enough in most calculations. If a situation where more precision is desired or required then more goes into getting more precise on the actual resistance in said application.The key one based ohm law and other on circular mil formula