winnie
Senior Member
- Location
- Springfield, MA, USA
- Occupation
- Electric motor research
The cable is a 12 gauge 50ft cable. The circuit that it is connected to is a 14 gauge circuit.
That's 50' of existing #12 to 200' of #14 remodel wiring, with electrical tape flying splices, and cut off EGC.It would not surprise me if a 1300W (10.8A) test load showed 7-10% voltage drop in a typical home wired with 14AWG wire.
I bet you can have runs of 14 AWG that are 250' of wire before they reach the panel.
My suggestion would be to stop using that cheap Klein circuit tester to measure voltage, and repeat your testing using the RMS meter for both measurements, at the breaker end and at the receptacle end. Also, measure the actual current draw of the heat gun, so that can be compared to a calculated drop with an assumed conductor length. You may find the voltage drop is normal once you have accurate measurements, especially if the branch circuits were installed with 14awg conductors.Hello, I have been trying to figure out this issue for a few days now and can't seem to pin down a reason.
The issue that's occurring is voltage drop at all receptacles in a home. The home has a 150A panel single phase. Normally I would assume a loose or improper connection of a neutral at the panel but this doesn't seem like the case. When measuring the circuit, when there is no load on the circuit the voltage is ~120V at breaker and receptacle. Under load the receptacle voltage will drop as low as ~99V i have measured. This is the case with every receptacle in the home on many different circuits. The interesting part for me is that at the receptacle I will measure ~109V under load but at the breaker I will measure ~120V. The wiring for each circuit is correct gauge for the correlating wired breakers 14 or 12 gauge. Some circuits in the home do have shared neutrals due to running a 3 wire and sharing the neutral but splitting the Black and red on separate breakers. This from my experience shouldn't be affecting anything but is something to note. Also circuits without shared neutrals still experience the same issue. I have measured 0-ohm resistance from the SE cable coming into the lugs on the main breaker and neutral to the correlating bus bars. It also seems the further distance the circuit is from the panel the larger the voltage drop and normally in a standard 2000sqft home voltage drop should be minimal on a circuit. I am just stuck on how I can get normal voltage leaving the breaker under load but at the device the voltage is significantly less. I have not opened my meter enclosure yet due to the weather but I am not sure if those connections could be contributing to the issue. Any tips or experience with diagnosing this issue would be amazing. Thanks.
No, but what is making up the other mentioned 175 feet of run. Part of the total run apparently is 14 AWG NM cable between the panel that shows no significant VD and a receptacle somewhere that has this 50 foot cord and possibly even more cord from what I get out of his information.@kwired , would you really expect 9V of drop with a 50 foot 12ga cord and a 10A load?
I would expect some voltage drop, but less than 2V.
-Jonathan
Here is an update for everyone, I went and cleaning the main feed coming into the panel because it had alot of extra old anti-oxident on the wires and i mean alot. Then wired a receptacle directly to the panel on a 15 amp breaker 1ft of 14 gauge from breaker to receptacle. I have then attached a brand new 14 gauge 100ft extension cord from the receptacle to the van. I am reading 120volts at the panel and 114.3 volts at the van under load of 6 amps. This now does look closer to normal voltage drop but still is a little lower than expected. Is this just other normal factors in play along with voltage drop. A ~2 volt difference from calculated to actual seems normal.Hello, I have been trying to figure out this issue for a few days now and can't seem to pin down a reason.
The issue that's occurring is voltage drop at all receptacles in a home. The home has a 150A panel single phase. Normally I would assume a loose or improper connection of a neutral at the panel but this doesn't seem like the case. When measuring the circuit, when there is no load on the circuit the voltage is ~120V at breaker and receptacle. Under load the receptacle voltage will drop as low as ~99V i have measured. This is the case with every receptacle in the home on many different circuits. The interesting part for me is that at the receptacle I will measure ~109V under load but at the breaker I will measure ~120V. The wiring for each circuit is correct gauge for the correlating wired breakers 14 or 12 gauge. Some circuits in the home do have shared neutrals due to running a 3 wire and sharing the neutral but splitting the Black and red on separate breakers. This from my experience shouldn't be affecting anything but is something to note. Also circuits without shared neutrals still experience the same issue. I have measured 0-ohm resistance from the SE cable coming into the lugs on the main breaker and neutral to the correlating bus bars. It also seems the further distance the circuit is from the panel the larger the voltage drop and normally in a standard 2000sqft home voltage drop should be minimal on a circuit. I am just stuck on how I can get normal voltage leaving the breaker under load but at the device the voltage is significantly less. I have not opened my meter enclosure yet due to the weather but I am not sure if those connections could be contributing to the issue. Any tips or experience with diagnosing this issue would be amazing. Thanks.
Here is an update for everyone, I went and cleaning the main feed coming into the panel because it had alot of extra old anti-oxident on the wires and i mean alot. Then wired a receptacle directly to the panel on a 15 amp breaker 1ft of 14 gauge from breaker to receptacle. I have then attached a brand new 14 gauge 100ft extension cord from the receptacle to the van. I am reading 120volts at the panel and 114.3 volts at the van under load of 6 amps. This now does look closer to normal voltage drop but still is a little lower than expected. Is this just other normal factors in play along with voltage drop. A ~2 volt difference from calculated to actual seems normal.
I agree, close enough.That sounds like normal voltage drop to me. The ~2V difference from calculated could be a combination of real world factors like the socket, meter error, load changes, etc.
And all very noticeable. Even to touch.Problems at the bus or breaker or even meter socket should drop the voltage at the breaker output terminal but OP isn't seeing any drop there.
The drop he is seeing is in the extension cord segment of the circuit. The last example he explained does have a short length of NM cable between the breaker and a receptacle. short enough it shouldn't really contribute any significant drop other than possibly because of poor contact/connections, but if they are poor enough they should warm up to at least an amount that likely is measurable with an infrared thermometer within a short time as well.
Quality of the extension cord could come into play as well. He says it is 14 AWG. Poor grade copper, maybe even little undersized to cheapen it? Poor connections to the end connectors? All such things will be additive.
You are describing a series circuit.Here is an update for everyone, I went and cleaning the main feed coming into the panel because it had alot of extra old anti-oxident on the wires and i mean alot. Then wired a receptacle directly to the panel on a 15 amp breaker 1ft of 14 gauge from breaker to receptacle. I have then attached a brand new 14 gauge 100ft extension cord from the receptacle to the van. I am reading 120volts at the panel and 114.3 volts at the van under load of 6 amps. This now does look closer to normal voltage drop but still is a little lower than expected. Is this just other normal factors in play along with voltage drop. A ~2 volt difference from calculated to actual seems normal.