Normally for single phase circuit voltage drop we use the following equation: (I * L * R / 1000) where I = load current, L = circuit length and R = resistance of the cable
For single phase, L = circuit length is equal to 2 * one-way length to account for the return length, so the equation can be re-written as (I * (one-way length * 2) * R / 1000).
For three phase circuit voltage drop we use the following equation: (1.732 * I * L * R / 1000) where I = load current, L = circuit length and R = resistance of the cable.
In this case is the length L one-way or two-way length? Taking a look at NEC Chapter 9 Table 9 calculation example, they are using a feeder with 100A continuous load, 240V source, 3 phase with a circuit length of 150 feet. They performed the following: Voltage drop (line to neutral) = 0.16 ohm * 150/1000 * 100A = 2.4V. To find line-to-line voltage drop they took 2.4V * 1.732 = 4.157V. Is this an error in the code? Should circuit length be multiplied by 2 here resulting in ~8.3V drop line-to-line? Does three phase circuit voltage drop only consider one-way length in the equation?