Looking to install 17 LED 120v bollard post lights along a 1000' driveway.
The posts that are spec'd are 28 watts. Using a voltage drop calculator I found online I did some quick trial and error calculations.
It looks like I can put the four lights furthest from the panel on a #12 thhn at 1 amp and suffer less than 5% voltage drop. Then I can put the next four furthest from the panel and suffer even less voltage drop. Then I can put the closest 9 lights at a little over 2 amps on a #12 and still suffer less than 5%.
I figure three runs, I can give them each their own neutral and fit it in a 3/4" PVC easily. Even at 40% allowed ampacity due to the # of CCC in the conduit they should meet code
Does this sound right? Am I being too cautious? Could I put the two furthest runs on the same circuit just with separate conductors from the breaker?
The posts that are spec'd are 28 watts. Using a voltage drop calculator I found online I did some quick trial and error calculations.
It looks like I can put the four lights furthest from the panel on a #12 thhn at 1 amp and suffer less than 5% voltage drop. Then I can put the next four furthest from the panel and suffer even less voltage drop. Then I can put the closest 9 lights at a little over 2 amps on a #12 and still suffer less than 5%.
I figure three runs, I can give them each their own neutral and fit it in a 3/4" PVC easily. Even at 40% allowed ampacity due to the # of CCC in the conduit they should meet code
Does this sound right? Am I being too cautious? Could I put the two furthest runs on the same circuit just with separate conductors from the breaker?