Michael Harkey
Member
I cannot find any language that exempts or treats differently, an AC system of 24Vrms in a health care facility, regarding voltage drop. I have a controls guy that routinely runs 24V controllers from a 24VAC 100VA transformer on long lengths of #18 wire with multiple devices on the same circuit, so that the last device on the branch sees only about 20V of the 24V if all were to operate at once (calculated). This is much more than 5% drop, and I can't find any exception for such low voltage systems to the 5% limit on voltage drop. Does anyone have thoughts on this, how the code might treat 24V and voltage drop that I just can't find?