In the case of a perfectly balanced set of 277V loads, there would be no current flow on the neutral, and you would get the correct answer by using the 480V three phase calculation, and then converting back to single phase, as George did in post #5. IMHO the only 'error' in that post was the use of 0.00193 ohms per foot for the wire; IMHO the wire is lightly loaded and thus cool, and thus a lower resistance would apply.
The the case of the _imbalanced_ load, Rattus has the technique right; figure out the current on the neutral, which will be the vector sum of the various phase currents. Apply this current to the resistance of the neutral conductor, which gives a _vector_ voltage for the neutral voltage drop. Depending upon the phase angle of this voltage relative to the phase voltages, this may increase or reduce the voltage that reaches the load.
However it is probably simpler and faster to use the approach of applying the 277V equation to each individual load, assuming no benefit from the shared neutral. This will over-estimate the voltage drop; so if you are good with the simplistic approach, then no need to do a more refined calculation.
Assuming/approximating the following:
0.5 ohm for 300 feet of single conductor
loads carry full load current (as if they were getting full voltage)
loads are all unity power factor
supply is 277V line-neutral.
I get:
276V phase A-neutral at the load
272V phase B-neutral at the load
267V phase C-neutral at the load
For what its worth, I estimate 6A flowing on the neutral, with a phase angle of 210 degrees.
-Jon
P.S. just saw rattus' last post. I used the spreadsheet ATAN2 function, which takes an X and Y input to give an angle, rather than Y/X to give a value. Eliminates the ambiguity of atan. I got -150 degrees, which I reported as 210 degrees. I then did my current calculations graphically with a CAD package. Oh, my estimate of 6A was really 6.25, so we agree there.
The the case of the _imbalanced_ load, Rattus has the technique right; figure out the current on the neutral, which will be the vector sum of the various phase currents. Apply this current to the resistance of the neutral conductor, which gives a _vector_ voltage for the neutral voltage drop. Depending upon the phase angle of this voltage relative to the phase voltages, this may increase or reduce the voltage that reaches the load.
However it is probably simpler and faster to use the approach of applying the 277V equation to each individual load, assuming no benefit from the shared neutral. This will over-estimate the voltage drop; so if you are good with the simplistic approach, then no need to do a more refined calculation.
Assuming/approximating the following:
0.5 ohm for 300 feet of single conductor
loads carry full load current (as if they were getting full voltage)
loads are all unity power factor
supply is 277V line-neutral.
I get:
276V phase A-neutral at the load
272V phase B-neutral at the load
267V phase C-neutral at the load
For what its worth, I estimate 6A flowing on the neutral, with a phase angle of 210 degrees.
-Jon
P.S. just saw rattus' last post. I used the spreadsheet ATAN2 function, which takes an X and Y input to give an angle, rather than Y/X to give a value. Eliminates the ambiguity of atan. I got -150 degrees, which I reported as 210 degrees. I then did my current calculations graphically with a CAD package. Oh, my estimate of 6A was really 6.25, so we agree there.
Last edited: