voltage drop question, residential

Status
Not open for further replies.

Stevenfyeager

Senior Member
Location
United States, Indiana
Occupation
electrical contractor
Most of my jobs requiring wire sizing due to voltage drop are a single cable going to a single load, such as a distant sub panel. My workers asked me about a lighting branch circuit in a very large house. Should we add all the lengths of NM cables on that circuit and if it totals say 150 - 200' or more, do we need to calculate the voltage drop like we do for single runs ? The lighting load is spread out, not like at the very end of a single run. Any advice ? Thank you.
 
For a rough idea, use half of the total circuit length.

If there's a lot of these, install a sub-panel.
 
You have to treat each branch individually and do the voltage drop calc for it. Depending how it's wired I would probably just upsize the home run. You're just trying to find how much resistance is between the source and the load.
 