Always learning here. So a lengthy run or multiple chimes like a 3-family house a 30va tranformer would be the way to go.
How is that possible to make work? to have a lighted button the switch needs to be closed if in series. It would work if you desired the button to light when the chime sounds - but will have a voltage drop across the light and through the chime to consider in the design, let alone VD over conductor length.I seem to remember that some door bell buttons had the light in series and if the light burned out, the door bell would not work.
That would account for a sizable voltage drop if that is the kind of switch being used.
I kind of thought he hinted that it possibly was with no load when he was reading 25 volts, but this has not been clarified either.You are forgetting that according to the OP the same 100' of wire with the leads twisted together at the button location produced 25V at the chime.
(Unless that was measured with the chime disconnected, maybe?)
Increasing source volts may very well get you by in many cases, though a higher VA rated transformer is the correct thing to do. You will as mentioned burn out more lamps in lighted buttons though.You do not increase the voltage with 2 chimes but rather you increase the VA. When we have 2 chimes I use a 16v 30va trany and it works fine. I suspect people use the tri tap trany where the 30va tap is 24V.
Something like this
Increasing source volts may very well get you by in many cases, though a higher VA rated transformer is the correct thing to do. You will as mentioned burn out more lamps in lighted buttons though.
I suspect that it is there only because otherwise people would ask "What would I get between those two terminals?"Interesting. Why 16V? What is the use of the 8v winding? I get that you can select either 16 or 24, but the way it's labeled suggests there's a use for 8v on its own as well.