A customer is renovating a loft above a barn to basically a small house. The barn is currently fed with 1AWG copper under a 125amp breaker from the main house which is about 400 ft away if not more. I did an optional load calculation which came out to 91amps. Should I be concerned with the load under a 125amp breaker and also voltage drop? Using a calculator by cerro wire i get the following. 400ft at 50 amps = 6.2v dropped at 120 and 240. I chose 50 because of load demand.
 

HuntNJ

Member
Location
NJ
Occupation
Electrician
also they have solar back feeding from the barn to the house. is this something i should be worried about. I dont know anything of solar
 